Forum index -> SCADA - Client -> configure the siemens LOGO! in eisbär editor
jacob configure the siemens LOGO! in eisbär editor
User
Registered at: 03.12.2018
Messages: 2

anyone who has experience with connecting the siemens LOGO! to eisbär. i found the LOGO component, but i cant get it to work, i've set up the ip for the logo, but cant find any device ID for the LOGO. 

06.06.2019 14:02
DanielBack Re: configure the siemens LOGO! in eisbär editor
User
Registered at: 16.11.2017
Messages: 164

Hello,

The Logo-component is only for Siemens LOGO! 8.FS4. The communication of the PLC is carried out via the network with the Modbus TCP protocol. Normaly, the device ID is 0. In the eisbaer help, you can find a step by step manual for the connection setup.


Mit freundlichen Grüßen Daniel Back
06.06.2019 15:19
jacob Re: configure the siemens LOGO! in eisbär editor
User
Registered at: 03.12.2018
Messages: 2

aah ok, so i have found the modbus TCP/IP driver, what file(s) do i need to import (in the modbus channel editor), is it a program save/backup from my LOGO!, im a little lost. 

and thank you very much for your help.

06.06.2019 15:39
DanielBack Re: configure the siemens LOGO! in eisbär editor
User
Registered at: 16.11.2017
Messages: 164

We have a special component for the LOGO!. You can find it in the component-list --> Driver.
Whith that driver, you are abel to connect every datapoint from the Logo. (see attached screenshots)


Mit freundlichen Grüßen Daniel Back
06.06.2019 16:22